How do I measure overhead signs and soffits above a beverage cooler row?
Give each overhead sign, soffit or suspended fitting a reference such as S2 for the sign. On the plan, mark its endpoints along the wall, its projection toward the aisle and the cabinet positions beneath it. Add an elevation showing the underside level measured from the same fixed height datum used for the cabinet tops. Match S2 to a photograph and a section through each affected cabinet. A general ceiling height does not show where a lower sign sits over part of the row.
The linked floor-level example places the JY-LC-318 top level at +1910 mm and the JY-FS-1D top level at +2030 mm. Suppose S2 has a level underside at +2200 mm and overlaps both cabinets in plan. The vertical gaps are 2200 - 1910 = 290 mm above C1 and 2200 - 2030 = 170 mm above C2. Label both gaps at their sections. These are illustrative planning gaps based on proposed body-bottom levels, not measured installed gaps or ventilation requirements. Where the sign underside is uneven, use its local level at each section. If a later survey measures the S2 underside at +2190 mm, record that dated observation separately from the drawn +2200 mm value. With the proposed C2 top still at +2030 mm, the gap becomes 2190 - 2030 = 160 mm. If the proposed C2 body bottom changes to +30 mm, its top becomes +2040 mm, and the gap becomes 2190 - 2040 = 150 mm. Both calculations use a measured sign level and a proposed cabinet top. A measured installed gap uses a measured cabinet top from the same datum.
Suppose S2 projects 250 mm from the rear wall toward the aisle. Draw that edge and each cabinet front and rear edge from the same wall reference. A 250 mm sign projection alone does not show its overlap with a cabinet whose position can change with front or rear alignment. Carry the selected alignment into the sections and revise the overlap when a cabinet moves. A positive vertical gap describes only the distance between the two levels at that section.
The recorded body heights are 1900 mm for JY-LC-318 and 2010 mm for JY-FS-1D and JY-FS-2D. Place each top using its own body-bottom level shown in the floor and support drawing. Compare the offered installation and maintenance spaces with the sections through S2. Retain S2 in later measurement and correction records. Show any proposed sign movement separately from the measured underside, and retain the original survey with its date. If a cabinet footprint moves, identify the floor readings at its new position and the revised sign overlap. Send the plan, elevation, sections, and referenced photograph through the inquiry with the affected cabinet labels and model codes.
Prepare this information
- S2 identifies the sign throughout the survey and revisions, with its underside and cabinet tops on one fixed height datum
- Each section shows its local vertical gap and horizontal overlap
- Dated underside and installed-top readings remain separate from proposed sign or cabinet movements
Record floor levels and cabinet alignment